Three days ago my upstairs air conditioning int stopped working. (This makes the listening room uninhabitable) The compressor and fan were not running but the recirculating fan was running. It was 86 upstairs. I checked the breaker, the voltage at the compressor and the condensate overflow switch. Everything was normal. Into our bedroom window went the air conditioner we have for emergencies. I called the service folks today. There is a huge backlog and the service manager suggested checking for 24V AC on the contactor, checking for a manual reset on the over pressure switch (I don't have one) and checking the capacitor. I had figured the cap was ok because neither the compressor nor the fan were running.
This is what I saw when I opened the service panel. The rounded top indicates complete failure. For reference, the top is horizontal when new. Often a bad electrolytic will bulge but I have never seen one this badly domed. I have seen both the top and bottom of electrolytic capacitors swollen, but never the side.
This is what I saw when I opened the service panel. The rounded top indicates complete failure. For reference, the top is horizontal when new. Often a bad electrolytic will bulge but I have never seen one this badly domed. I have seen both the top and bottom of electrolytic capacitors swollen, but never the side.